LOAD KING WIRE INDUSTRIES


L.T. PVC INSULATED POWER AND CONTROL CABLE 1.1 kv grade

PROCESS

LT HEAVY DUTY CABLES

These cables are suitable for use on Ac single phase systems for the rated volatge up to and including 1100 volts.These cables can be used on DC system for rated voltage up to and including 1500 volts on earth.

CONDUCTOR
The most acceptable metals for conductors are copper and aluminium due to their higher conductivity and ductility . As copper has got higher affinity for sulphur , it corrodes in the atmosphere where shulphur fumes are present . In these conditions tinned copper should be used.

Aluminium oxide film which is always present on alminium surface  acts as a barrier and it protects the aluminium  conductor from corrosion in fumes laden atmosphere.
 

CONDUCTOR CONSTRUCTION
The most economical construction is solid conductor  i.e. conductor  is made of one single wire as the  area of connductor increase s, soilid conductor becomes more stiff and hence dificult to handle. In this case stranded construction is adopted. Here the conductor is made of numbers of strands. The strands are arranged in spiral layers in 1+6+12 +18+......  formations. this construction provides more flexibility. Where crimping of lugs are required, the conductor has to be of stranded construction only .

To economise  in insulating material, weight and overall diameter, shaped conductor are employed in bigger sized cables. Here the strande conductor is shaped in to a segment of a circle so that when all  the cores are laid they form a complete circle.
 

INSULATION
The PVC (Polyvinyl Cholride) covering over conductors is called insulation and is provided by extrusion process only. The insulated conductor is called core . We are using two types of compound for insulation  :-

*  Insulation with PVC compound which is suitable for 70o C continuos operation.

*  Insulation with PVC compound which is suitable for 85oC continious operation.
 

The follwing colour code is used for identification :-

   Single core            : Red, Black, Yellow or Blue
   Two cores              : Red and black
   Three cores           : Red ,Yellow ,and blue
   Three & half          :  Red, Yellow Blue  and Reduced neutral Black
    Four Core             : Red , Yellow, Blue, and black
    Five core               : Red , Yellow, Blue , Black and Grey.
    Six Core                : Two adjacent cores Blue and Yellow (Counting and direction core)
                                     and remaining Grey in each layer.
 

OUTERSHEATH
The PVC covering on armouring in case of armoured cable and over the inner sheath in case and over the innersheath in case of unarmoured cables is called outer sheath.

1.Outer sheath with PVC compound which is siutable for 70 degree continious operation
2.Outer sheath with PVC compound which is suitable for 80 degree continious operation.

PVC has got fire retarding properties due to it's halogen content.The fire in the cable gets extinguished immediately on removal of the source.

DELIVERY LENGTH
The cables are generally delivered in 100 Mtrs.coils wrapped with Polythylene/Hessian.The bigger size cables are supplied on wodden frames.
 

LT HEAVY DUTY CABLES FOR FIXED WIRING AND CABLE OPERATION
These cables are suitable for use on AC single phase or three phase systems for rated voltage of upto or including 1100 volts.These cables can be used on DC systems for rated voltage of upto or including 1500 volts.

CONDUCTOR
 The most acceptable metals for conductors are copper and alumimnium due to there higher conductivity and ductility.As copper has higher affinity for Sulphur it corrodes in atmosphere where Sulphur fumes are present.In such cases tinned Copper must be used.

CONDUCTOR CONSTRUCTION
The most economical construction for conductors is solid conductors i.e conductor
is made of one single wire.As the area of the conductor increases,solid conductor becomes more stiff and difficult to handle.In this case use stranded in rope construction is used for cables.Where crimping of lugs are required the conductor has to be stranded or bunched construction only.

As per the international convention the size of the cable is decided by it's resistance only.The constructions of the conductor mentioned in the table are only for  guidance and as per market
convention.

INSULATION
The PVC(Poly Vinyl Chloride) covering over the conductor is called insulation and is provided by extrusion process.The insulated conductor is called the core.The insulation is suitable for 70 degree celcius.

The following colour code is used for identification:-
 
 
          CORE CABLE FOR FIXED WIRING FLEXIBLE CABLES
1 Core Red,Black,Yellow,Blue,White or Grey Red,Black,Yellow,White or Grey
2 Core Red and Black Red and Black
3 Core Red,Yellow,Blue Red,Yellow,Blue
4 Core Red,Yellow,Blue and Black Red,Yellow,Green,Blue
5 Core Red,Yellow,Blue,Black,Grey Red,Yellow,Blue,Black,Green
6 Core 2 adjacent cores Blue and Yellow 
(counting and direction cores) and remai 
ning grew in each layer

 

Laying Up
The cables are laid up with suitable lay.The final layer always has a right hand lay i.e if you look along the cables the cores moves to right hand.

Inner Sheath
Inner sheath is provided over the laid up cores.It is provided to give circular shape to the cable and it provides bedding and armouring.

The International standars permit following two methods of applying the inner sheath of any thermoplastiv material i.e PVC Polythene etc.

EXTRUDED INNER SHEATH
Here the inner sheath is provided by extrusion of thermoplastic over  the laid cores.  This type of  the inner sheath is generally provided in cables having round cores i.e in control cables and power cables upto 10 Sq.mm size.

This type of inner sheath also acts as a water barrier between the cores and outer sheath.In case of any punture the  water cannot reach the inner cores and hence we recommend that cables for outdoor underground uses should uses should have extruded inner sheath.

TAPPED INNER SHEATH
Here  the inner sheath is provided by wrapping a thermoplastic tape over the laid up cores.It is generally employed in the cables having sector cores i.e muticore cables of 16 Sq.mm and above.
This method saves a process and hence manufacturing always provides this type of inner sheath unless the purchase specification ask for extruded inner sheath.

ARMOURING
In case of armoured cables,generally galvanised steel wires/strip armouring  is provided over the inner sheath in multicore cables and the insulation in the single core cables.It provides mechanical protection to inside cores and it carries earth return current in case of a short circuit of a core with armoured.
The round wire armouring is provided in cable where caculated diametre under armour is upto 13 Sqmm. Above this,the armouring is either with the round wire  or strip of size 4mm x 0.80 mm. As strip construction is economical, the manufacturer always provide steel strip armouing is specially specified.

In long run of cables and in case of mines, round wire armouring is must as strip construction provides higher resistance to earth fault current and some times this current may not be sufficient to operate the circuit breaker in case  of earth fault.

In mines, the resistance of the armour in no case should be more than twice the resistance of main core for safety reasons. To achive this, sometimes tinned hard drawn copper wire are required to used alongwith galvanised steel wire. Sometimes two layers of steel are provided to give extra protection.

In case of single core armoured cables for use in DC circuit , the material for armouring has to be non magnetic , as in this case the return current is not passing through the same cable and hence it will not cancel the magnetic lines produced by the current .These magnetic lines which are oscillating in case of Ac current will give rise to eddy current in magnetic current in magnetic armouring and hence armouring will become hot, and this may lead to the failure of the cable. Generally hard draw aluminium wire / strip are used for armouring in this case.
 

LAYING UP
In case of multi core cables the cores are laid up with suitable lay.

SHEATH
The PVC coating on core in case of single core cable and o laid up cores in case of multi core cables is SHEATH.It is PVC compound suitable for 70oC continious operation.

SHEATH COLOUR
The colour of sheath is generally black .We may supply other colour also on request.

DELIVERY LENGTH
The cables are generally delivered in 100 Mtrs coil wrapped with Poly ethylene/Hessian. The bigger size cable are supplied on wooden drums.
 

 LT HOUSEHOLD WIRE
The cables are suitable for use on AC single phase (earthed or unearthed )
systems for rated voltage up to and including 650 volts.
 

CONDUCTOR
The most acceptable metals for conductors are copper and aluminium due to their higher conductivity and ductility . As copper has got higher affinity for shulphur. It corrodes in the atmosphere where sulphur fumes are present . In these conditions tinned copper should be used .
 

CONDUCTOR CONSTRUCTION :
In this types of cables, the stranded and bunch construction of copper is  adopted . Here the conductor is made of number of stands. Number of stands are as follows :
 
 
 
 
Size in sq. mm. Minimum number of wire in the conductor 
Cu                                    Al 
1.0  3                                     - 
1.5  3                                     3 
2.5  3                                     3 
4.0  7                                     3 
6.0  7                                     3 
10.0  7                                     7 

 

INSULATION
The PVC  (Polyvinyl choloride ) covering over conductor is called insulation
and it provided by extrusion process. The insulation is suitable for 70o C continious operation.
 

COLOUR OF INSULATION
The insulation is available in many colours like Red Blue ,Black, Yellow, White, Grey etc. Any special colour is also available if specialy specified .
 

DELIVERY LENGTH
The cables are delivered in 100 Mtrs coils wrapped with Polyethelyne/Hessian.Wooden drum packing is also available on demand of special length.
 

PVC INSULATED TELECOMMUNICATION CABLE FOR TELECOM SIGNALS.

The cables are suitable for telephone connection, EPABX or PBX
system. The cables are suitable for use on DC baterry systems.

CONDUCTOR
The conductor is annealed , tinned electrolytic high conductive copper wire.
The conductor is always used in solid condition.

INSULATION
 The PVC (Polyvinyl Chloride) covering over the conductor is called insulation and is provided by extrusion process only. The insulated conductor is called core. The insulation is suitable for 70o C continious operation.
 

TWINNING (TWISTING)
The two insulated conductors which is called pair is uniformly twisted together with a right hand lay. The twisted pair laid up to form a symmetrical and compact cable, now the pairs stranded and twisted in left hand lay for making a multipair.
 

COMMON COVERING
The cable (laid up pair ) is tightly lapped with a PVC tape applied with an overlap of 30% . This facilities is not available in single pair.
 

IDENTIFICATION THREAD
A rip cord is laid through out the length of the cable either below the sheath or below the tape .
 

ARMOURING
In case of armoured cables, generally galvanised steel wire/strip armouring is provided over the laid up pairs (Over the common covering of tape ) in the multipair cables.
 

SHEATH OR OUTER COVERING
The PVC coating on core in case of single pair cable and on laid up cores in case of multi pair cables is called SHEATH. It is PVC compound suitable for 70o C continious operation.

In case of single pair, The two insulating conductors of the pair are laid side by side and sheathed . In case of multi pair (either armoured or unarmoured ) is sheathed by Extruded process.
 

COLOUR OF SHEATH
The colour of the sheath in single pair and in case of unarmoured multipaired is grey, but in case of armoured cables it is available in black colour .
 

DELIVERY LENGTH  :
The cables are generally delivered in 100 Mtrs. coils wrapped with Polyethylyne / Hessian . The bigger size cables or cables in bigger length are supplied in wooden drums.