L.T. PVC INSULATED POWER AND CONTROL CABLE 1.1 kv grade
| PROCESS |
LT HEAVY DUTY CABLES
These cables are suitable for use on Ac single phase systems for the rated volatge up to and including 1100 volts.These cables can be used on DC system for rated voltage up to and including 1500 volts on earth.
CONDUCTOR
The most acceptable metals for conductors are
copper and aluminium due to their higher conductivity and ductility . As
copper has got higher affinity for sulphur , it corrodes in the atmosphere
where shulphur fumes are present . In these conditions tinned copper should
be used.
Aluminium oxide film which is always present on
alminium surface acts as a barrier and it protects the aluminium
conductor from corrosion in fumes laden atmosphere.
CONDUCTOR CONSTRUCTION
The most economical construction is solid conductor
i.e. conductor is made of one single wire as the area of connductor
increase s, soilid conductor becomes more stiff and hence dificult to handle.
In this case stranded construction is adopted. Here the conductor is made
of numbers of strands. The strands are arranged in spiral layers in 1+6+12
+18+...... formations. this construction provides more flexibility.
Where crimping of lugs are required, the conductor has to be of stranded
construction only .
To economise in insulating material, weight
and overall diameter, shaped conductor are employed in bigger sized cables.
Here the strande conductor is shaped in to a segment of a circle so that
when all the cores are laid they form a complete circle.
INSULATION
The PVC (Polyvinyl Cholride) covering over conductors
is called insulation and is provided by extrusion process only. The insulated
conductor is called core . We are using two types of compound for insulation
:-
* Insulation with PVC compound which is suitable for 70o C continuos operation.
* Insulation with PVC compound which is
suitable for 85oC continious operation.
The follwing colour code is used for identification :-
Single core
: Red, Black, Yellow or Blue
Two cores
: Red and black
Three cores
: Red ,Yellow ,and blue
Three & half
: Red, Yellow Blue and Reduced neutral Black
Four Core
: Red , Yellow, Blue, and black
Five core
: Red , Yellow, Blue , Black and Grey.
Six Core
: Two adjacent cores Blue and Yellow (Counting and direction core)
and remaining Grey in each layer.
OUTERSHEATH
The PVC covering on armouring in case of armoured
cable and over the inner sheath in case and over the innersheath in case
of unarmoured cables is called outer sheath.
1.Outer sheath with PVC compound which is siutable
for 70 degree continious operation
2.Outer sheath with PVC compound which is suitable
for 80 degree continious operation.
PVC has got fire retarding properties due to it's halogen content.The fire in the cable gets extinguished immediately on removal of the source.
DELIVERY LENGTH
The cables are generally delivered in 100 Mtrs.coils
wrapped with Polythylene/Hessian.The bigger size cables are supplied on
wodden frames.
LT HEAVY DUTY CABLES FOR FIXED WIRING AND CABLE
OPERATION
These cables are suitable for use on AC single
phase or three phase systems for rated voltage of upto or including 1100
volts.These cables can be used on DC systems for rated voltage of upto
or including 1500 volts.
CONDUCTOR
The most acceptable metals for conductors
are copper and alumimnium due to there higher conductivity and ductility.As
copper has higher affinity for Sulphur it corrodes in atmosphere where
Sulphur fumes are present.In such cases tinned Copper must be used.
CONDUCTOR CONSTRUCTION
The most economical construction for conductors
is solid conductors i.e conductor
is made of one single wire.As the area of the
conductor increases,solid conductor becomes more stiff and difficult to
handle.In this case use stranded in rope construction is used for cables.Where
crimping of lugs are required the conductor has to be stranded or bunched
construction only.
As per the international convention the size of
the cable is decided by it's resistance only.The constructions of the conductor
mentioned in the table are only for guidance and as per market
convention.
INSULATION
The PVC(Poly Vinyl Chloride) covering over the
conductor is called insulation and is provided by extrusion process.The
insulated conductor is called the core.The insulation is suitable for 70
degree celcius.
The following colour code is used for identification:-
| CORE | CABLE FOR FIXED WIRING | FLEXIBLE CABLES |
| 1 Core | Red,Black,Yellow,Blue,White or Grey | Red,Black,Yellow,White or Grey |
| 2 Core | Red and Black | Red and Black |
| 3 Core | Red,Yellow,Blue | Red,Yellow,Blue |
| 4 Core | Red,Yellow,Blue and Black | Red,Yellow,Green,Blue |
| 5 Core | Red,Yellow,Blue,Black,Grey | Red,Yellow,Blue,Black,Green |
| 6 Core | 2 adjacent cores Blue and Yellow
(counting and direction cores) and remai ning grew in each layer |
Laying Up
The cables are laid up with suitable lay.The
final layer always has a right hand lay i.e if you look along the cables
the cores moves to right hand.
Inner Sheath
Inner sheath is provided over the laid up cores.It
is provided to give circular shape to the cable and it provides bedding
and armouring.
The International standars permit following two methods of applying the inner sheath of any thermoplastiv material i.e PVC Polythene etc.
EXTRUDED INNER SHEATH
Here the inner sheath is provided by extrusion
of thermoplastic over the laid cores. This type of the
inner sheath is generally provided in cables having round cores i.e in
control cables and power cables upto 10 Sq.mm size.
This type of inner sheath also acts as a water barrier between the cores and outer sheath.In case of any punture the water cannot reach the inner cores and hence we recommend that cables for outdoor underground uses should uses should have extruded inner sheath.
TAPPED INNER SHEATH
Here the inner sheath is provided by wrapping
a thermoplastic tape over the laid up cores.It is generally employed in
the cables having sector cores i.e muticore cables of 16 Sq.mm and above.
This method saves a process and hence manufacturing
always provides this type of inner sheath unless the purchase specification
ask for extruded inner sheath.
ARMOURING
In case of armoured cables,generally galvanised
steel wires/strip armouring is provided over the inner sheath in
multicore cables and the insulation in the single core cables.It provides
mechanical protection to inside cores and it carries earth return current
in case of a short circuit of a core with armoured.
The round wire armouring is provided in cable
where caculated diametre under armour is upto 13 Sqmm. Above this,the armouring
is either with the round wire or strip of size 4mm x 0.80 mm. As
strip construction is economical, the manufacturer always provide steel
strip armouing is specially specified.
In long run of cables and in case of mines, round wire armouring is must as strip construction provides higher resistance to earth fault current and some times this current may not be sufficient to operate the circuit breaker in case of earth fault.
In mines, the resistance of the armour in no case should be more than twice the resistance of main core for safety reasons. To achive this, sometimes tinned hard drawn copper wire are required to used alongwith galvanised steel wire. Sometimes two layers of steel are provided to give extra protection.
In case of single core armoured cables for use
in DC circuit , the material for armouring has to be non magnetic , as
in this case the return current is not passing through the same cable and
hence it will not cancel the magnetic lines produced by the current .These
magnetic lines which are oscillating in case of Ac current will give rise
to eddy current in magnetic current in magnetic armouring and hence armouring
will become hot, and this may lead to the failure of the cable. Generally
hard draw aluminium wire / strip are used for armouring in this case.
LAYING UP
In case of multi core cables the cores are laid
up with suitable lay.
SHEATH
The PVC coating on core in case of single core
cable and o laid up cores in case of multi core cables is SHEATH.It is
PVC compound suitable for 70oC continious operation.
SHEATH COLOUR
The colour of sheath is generally black .We may
supply other colour also on request.
DELIVERY LENGTH
The cables are generally delivered in 100 Mtrs
coil wrapped with Poly ethylene/Hessian. The bigger size cable are supplied
on wooden drums.
LT HOUSEHOLD WIRE
The cables are suitable for use on AC single
phase (earthed or unearthed )
systems for rated voltage up to and including
650 volts.
CONDUCTOR
The most acceptable metals for conductors are
copper and aluminium due to their higher conductivity and ductility . As
copper has got higher affinity for shulphur. It corrodes in the atmosphere
where sulphur fumes are present . In these conditions tinned copper should
be used .
CONDUCTOR CONSTRUCTION :
In this types of cables, the stranded and bunch
construction of copper is adopted . Here the conductor is made of
number of stands. Number of stands are as follows :
| Size in sq. mm. | Minimum number of wire in the conductor
Cu Al |
| 1.0 | 3 - |
| 1.5 | 3 3 |
| 2.5 | 3 3 |
| 4.0 | 7 3 |
| 6.0 | 7 3 |
| 10.0 | 7 7 |
INSULATION
The PVC (Polyvinyl choloride ) covering
over conductor is called insulation
and it provided by extrusion process. The insulation
is suitable for 70o C continious operation.
COLOUR OF INSULATION
The insulation is available in many colours like
Red Blue ,Black, Yellow, White, Grey etc. Any special colour is also available
if specialy specified .
DELIVERY LENGTH
The cables are delivered in 100 Mtrs coils wrapped
with Polyethelyne/Hessian.Wooden drum packing is also available on demand
of special length.
PVC INSULATED TELECOMMUNICATION CABLE FOR TELECOM SIGNALS.
The cables are suitable for telephone connection,
EPABX or PBX
system. The cables are suitable for use on DC
baterry systems.
CONDUCTOR
The conductor is annealed , tinned electrolytic
high conductive copper wire.
The conductor is always used in solid condition.
INSULATION
The PVC (Polyvinyl Chloride) covering over
the conductor is called insulation and is provided by extrusion process
only. The insulated conductor is called core. The insulation is suitable
for 70o C continious operation.
TWINNING (TWISTING)
The two insulated conductors which is called
pair is uniformly twisted together with a right hand lay. The twisted pair
laid up to form a symmetrical and compact cable, now the pairs stranded
and twisted in left hand lay for making a multipair.
COMMON COVERING
The cable (laid up pair ) is tightly lapped with
a PVC tape applied with an overlap of 30% . This facilities is not available
in single pair.
IDENTIFICATION THREAD
A rip cord is laid through out the length of
the cable either below the sheath or below the tape .
ARMOURING
In case of armoured cables, generally galvanised
steel wire/strip armouring is provided over the laid up pairs (Over the
common covering of tape ) in the multipair cables.
SHEATH OR OUTER COVERING
The PVC coating on core in case of single pair
cable and on laid up cores in case of multi pair cables is called SHEATH.
It is PVC compound suitable for 70o C continious operation.
In case of single pair, The two insulating conductors
of the pair are laid side by side and sheathed . In case of multi pair
(either armoured or unarmoured ) is sheathed by Extruded process.
COLOUR OF SHEATH
The colour of the sheath in single pair and in
case of unarmoured multipaired is grey, but in case of armoured cables
it is available in black colour .
DELIVERY LENGTH :
The cables are generally delivered in 100 Mtrs.
coils wrapped with Polyethylyne / Hessian . The bigger size cables or cables
in bigger length are supplied in wooden drums.